I’ve successfully installed a Networx panel (NX-8E) and connected to the Vera via the built-in rs232 interface.
The panel has a zone extender installed, and I am using zones 1-19. Vera detected all of them (including the correct zone names). I’ve added 1-4 and 11-18, i.e. created devices for those in the vera.
The problem I’m seeing is that each time Zone 18 is tripped (staircase door), zones 1-4 and 11-16 are reset, i.e. tripped=0, even though some zones are in fact tripped.
I’ve added a commented log (lines starting with *** are my comments). The problem appears to be after the line starting with ******: zones 1-4 and 11-16 (but not 17 and 19!) are reported as not triggered (even though zones 1 and 2 are triggered). Unlike for other zone reporting, these reports are not preceded by individual zone status messages from the Networx panel.
Before I dive into the source code I’d appreciate any pointers I can receive!
Apologies if this is a known issue or a setup error. Many thanks!