Getting Fortrezz WV-01 water valve to work

I hope you can help me.
I am trying to get my Fortrezz WV-01 water valve to work and be recognized with my Vera 3, U15, 1.5.622.
The valve is recognized as a light switch, I have tried the default switch setting.
I have also tried urn:schemas-micasaverde-com:device:Relay:1 with D_Relay1.xml

When the water valve in included the hard wired water sensor probe does not work, it works when excluded from the Vera 3.
Vera does show the correct status, i.e. if it is open or closed.
I do not know how can query the status of the water valve.

Does anyone know how to get Vera to recognize the water valve correctly?

It’s not easy to understand but here is the first step.
Fortrezz page 6 - 7 instructions, Water Alarm Mode or Water Level Mode.
Which one is yours set to?
Check on the Vera Dashboard, Water Valve Module, Device Options, Variable.
Is it set to 1, Water level Mode?
Is it set to 0, Water Alarm Mode?

Note Page 6, Item 7: The local water probe connected to the Water Valve will only operate in Water level Mode when the Water Valve is not in a network.

Does this make sense so far???

Which mode do you want?

Hi miagrip
You hit my issue on the head.
I was in water level mode which is why the wired probe did not work.
Changed to water alarm mode, which I want and the probe now works.
All happy now.
Thank you.

Does anyone have experience with these valves operating with Vera? It seems that we had setup problems but no installation success stories? Do these work well as emergency shutoff valves?

Don

Mine works well in an emergency. A couple of times leaks from hair etc from the door of a washing machine and another detected a leak from my hot water heat pump. The valve shuts off, the siren / strobe goes off and I get messages and emails that it has tripped. I wired a switch into the face of the Fortrezz siren to turn it off for a while so we can find the problem. When the batteries go low in the detectors it also warns you. Works for me…

Hi bd8134

Thanks for the information. It doesn’t seem that they are overly used. I guess the high price discourages wider adoption. Did you have it installed before or after the main water cutoff? In other words, is there still a house cutoff between the value and the city water supply?

Don

Yes they are pricey but I did not want something that seemed like it would not last or was not robust, hopefully should stand the test of time. The Fortrezz water valve is between my main water shutoff and my faucets etc. So I can turn off my main water shutoff and work on the Fortrezz valve if necessary. I think this is the way Fortrezz recommend it is installed.

Hi bd8134

Great… Thanks

Don

Hello Folks,

I have installed one to fill my bathtub… (fortrezz wv-01)

but I can not open and close the valve, it appears like a switch light in my dashboard but do not works opening and closing the valve…

what I can change to solve this ?

using vera 3 with UI5 1.5.622

thanks for help…

Check out this thread… [url=http://forum.micasaverde.com/index.php/topic,5644.msg137098.html#msg137098]http://forum.micasaverde.com/index.php/topic,5644.msg137098.html#msg137098[/url]
It should help as to what mode you are in and what settings you can change according to your application.
It is also in the manual.

I do not have the manual, was lost…

thanks for help

I want to use to open and close water…only…and if the bathtube is full close the valve…

is it possible
with you experience can you elaborate a set for this ?

thanks in advance …

See Page 6. Fortrezz WV-01 Manual.

By default these valves are in water alarm mode and they cannot be opened via Z-Wave. You need to change it to water level mode.

Parameter 0 (1 Byte hex) Value == FF

Also note the wired probe will not work when in Water Level Mode after it has been added to Vera.
What will you use to monitor water level?
I would also consider some sort of battery backup because in case of a power failure, the valve will not be able to close.
Something like a heating zone valve which normally closes when its 24v is removed could be an alternative.

Then when controlling open and close functions by Vera, I lost the function of level monitoring ?

this way I have to buy another zwave water detector…

I think this is a serious problem or limitation of the product…when added to vera lost your capacities…

I have a dumb newbie question: I’ve installed a Fortrezz WV-01 water valve and have enrolled it into my new Vera Edge UI7 system. It appears as a light switch. Although I am able to open and close the valve, when the valve is open, the light switch indicates Off; when the valve is closed, the light indicates On. This is the opposite of what is desired. How can this be corrected? Thanks in advance for your assistance.

UPDATE: After contacting Vera and enabling remote tech support, they modified the device to make it a relay rather than a switch. It now indicates correctly. However, it still appears as a light on the mobile app.

Tech Support modified it after inclusion by changing the .xml and .json files, from the device?s control panel under the Advanced tab > Params. The correct names it should have are, D_Relay1.xml and D_Relay1.json .

[quote=“MiSkyPig, post:15, topic:176288”]I have a dumb newbie question: I’ve installed a Fortrezz WV-01 water valve and have enrolled it into my new Vera Edge UI7 system. It appears as a light switch. Although I am able to open and close the valve, when the valve is open, the light switch indicates Off; when the valve is closed, the light indicates On. This is the opposite of what is desired. How can this be corrected? Thanks in advance for your assistance.

UPDATE: After contacting Vera and enabling remote tech support, they modified the device to make it a relay rather than a switch. It now indicates correctly. However, it still appears as a light on the mobile app.

Tech Support modified it after inclusion by changing the .xml and .json files, from the device?s control panel under the Advanced tab > Params. The correct names it should have are, D_Relay1.xml and D_Relay1.json .[/quote]

Hi–

Thanks… that’s a big help

Don

[quote=“MiSkyPig, post:15, topic:176288”]I have a dumb newbie question: I’ve installed a Fortrezz WV-01 water valve and have enrolled it into my new Vera Edge UI7 system. It appears as a light switch. Although I am able to open and close the valve, when the valve is open, the light switch indicates Off; when the valve is closed, the light indicates On. This is the opposite of what is desired. How can this be corrected? Thanks in advance for your assistance.

UPDATE: After contacting Vera and enabling remote tech support, they modified the device to make it a relay rather than a switch. It now indicates correctly. However, it still appears as a light on the mobile app.

Tech Support modified it after inclusion by changing the .xml and .json files, from the device?s control panel under the Advanced tab > Params. The correct names it should have are, D_Relay1.xml and D_Relay1.json .[/quote]

All–

In the water level mode there is a period during which time the WV-01 cannot be remotely (i.e., through vera) be turned back on (i.e., valve re-opened). The manual says it is 60 minutes is the default. Does anyone know how to change that timeout period? (It seems longer than 60 minutes).

Thanks in advance for your help.

Don

The default value to turn the valve on is 60 minutes according to the manual, never tried it.
[url=http://www.fortrezz.com/index.php/component/jdownloads/finish/3/3?Itemid=0]Ezlo - Property Empowered
Parameter 1 page 8.
It can be changed if the valve is included into Vera.

Go back into the device, Device Options, and read what value the valve has returned for parameter 1.
I believe you should get 60, never tried it.

To change mode, ‘Add configuration setting’, Variable - 1, Data size - 1 byte hex, Desired Value - “0” or for how many minutes delay you want.

Let us know how you get on.

[quote=“bd8134, post:18, topic:176288”]The default value to turn the valve on is 60 minutes according to the manual, never tried it.
[url=http://www.fortrezz.com/index.php/component/jdownloads/finish/3/3?Itemid=0]Ezlo - Property Empowered
Parameter 1 page 8.
It can be changed if the valve is included into Vera.

Go back into the device, Device Options, and read what value the valve has returned for parameter 1.
I believe you should get 60, never tried it.

To change mode, ‘Add configuration setting’, Variable - 1, Data size - 1 byte hex, Desired Value - “0” or for how many minutes delay you want.

Let us know how you get on.[/quote]

Hi bd8134

Thanks for your input. That got me focused on the correct parameters. One correction:

To change mode, should be: ‘Add configuration setting’, Variable - 1, Data size - 2 bytes hex, Desired Value - “0” or for how many minutes delay you want.

Note the 2 bytes hex vice the 1 byte hex. Took me a while to figure it out…

Don