I am looking to integrate my smoke alarms into vera. I would like to be able to use them as a burglar alarm and trigger them as needed.
I have done quite a bit of reading on this but am still a bit in the dark as to how exactly I need to do this. My smoke alarms are wired with 3 wires. black(120v), white(neutral), red(intercommunication).
From what I have read I need to send a 9volt signal over the red line and this will trigger the alarm. However, I am an amateur when it comes to dealing with relays and what not. My first thoughts were to use some kind of switch/relay and a 9v DC battery but then after a lot of thinking it made me realize that I probably don’t want to have to change the batteries on this every so often…I’d like a more permanent ‘wired’ solution.
I’ve looked into a few of the Zwave relays from Linear, Evolve, and Remotec but I am not sure which one would be appropriate for the 9v necessary. Also, I need a bit of help from someone to help me draw up a quick diagram or schematic so that I can make sure I am on the right path.
Any help/info/pictures/advice/schematics that you guys can provide would be greatly appreciated!
Thanks but I am going to do it. Of course I am going to be testing everything every step of the way. @RichardTSchaefer has had success doing exactly what I am describing and it’s done in a lot of corporate offices too. My cousin who is an electrician in NY has a very similar setup where his fire alarms tie in with burglar alarm.
I wouldn’t start this project without a multimeter to read verify every wire and doing the whole project in progressive small steps. I appreciate your concern but as stated above I am going to verify & test repeatedly that nothing breaks along the way.
The problem with the z-wave sirens is that I live in a very big house and I would need to add one to every room in my house for it to be “effective”… which gets expensive fast! With this method I would only need to tap into 1 smoke alarm and by sending a 9v signal across the red wire it would make ALL of the smoke alarms trigger. It is much cheaper and a lot more effective. As long as I cross my t’s and dot my i’s there should not be any issue.
I have 5 smoke (Dual Smoke + CO2) detectors in the house/garage.
They are all tied together. (Black, White, Red Wires). If one goes off … they all go off.
I have a Kidde SM120X relay that senses if any Smoke detectors is tripped (This is also connected to the Black, White, Red wires).This closes the relay, the relay contacts trip a Alarm System Zone.
I also have one relay contact from my ITach that places the +9V on Red Wire and -9V on the white wire.
This trips all of the smoke detectors as well as the Alarm System. The other two relays of the iTach pulse the battery powered door opener for my two garage doors.
The Kidde has a 9V output that could have been used to trip the smoke detectors. But I have the Kidde installed near the smoke detector near the Alarm System and the iTack near a smoke detector in the Garage.
So I can sense my smoke detectors going off as well as I can trip the smoke detectors.
I do the latter to test the smoke detectors and when I really need to get one’s attention.
That would be used for detecting when the alarm goes off.
My primary focus right now is to be able to trigger an alert. Kinda want to stay away from a battery because I don’t want to have another thing to worry about changing.
I am thinking to buy a 9V DC regulated power supply and cutting off the end and tying the positive/negative into the red/white
Based on my research, this should work with a combination or AC or battery operated detectors that are interconnected, as long as the relay is used on an AC powered detector. Since I have to replace all my smoke detectors, I will go down this path.
My local building code requires AC connected Smoke detectors.
I actually have Battery with AC Backup/Charge. Our code might require the combo.
I am sure the relay does not use the signaling wire for power.
So it should only look like a single smoke detector to which ever device is actually signaling.
I believe the specifications for these Smoke Detectors is that they can signal 8 to 10 other connected units.
Sorry about the fuzziness of my answers … I did my research a long time ago … and I am getting old …
In case anyone is curious I was able to get this going by using a 9V ‘regulated’ DC power supply. I did have trouble finding one with an appropriate cable length (~10ft) and was worried about degrading the voltage by adding an gauge extension. I learned that 9V DC regulated power supplies are used a lot in audio equipment for pedals and what not and generally require a decent length. I went down to my local Guitar Center and sure enough they have a 10ft 9V DC regulated power supply. (Made by 1SPOT in case you are curious)
I first used my multimeter to verify the voltage on the wires while it was going off through a legitimate ‘button press test’ and to make sure I was going to hook into. After verifying this I turned off the power to the smoke alarms in the breaker.
I cut off the end and split the wires apart stripped the ends. Using the multimeter I determined which end was positive & which was negative. I trimmed 1 to be shorter than the other to prevent them from accidentally coming into contact.
I had to separate the smoke alarm to open it up and drill a small hole in the plastic in an empty space to allow me to fish the wires through cleanly and not disturb the clean fit that the back of the smoke alarm has to the ceiling.
I then wired the positive into the red/orange intercommunication wire and the negative into the white neutral wire group.
After verifying my wiring I flipped the breakers back on and plugged it in. Within 3 seconds of plugging it in the alarm is tripped on all smoke alarms. After removing the power completely it takes about 10-15secs to disengage.