Trane thermostat "Fan type" setting Gas(??) or Electric?

With cooler temperatures, my heat is coming on. I noticed that the furnace is short cycling. I noticed that the Trane thermostat would turn on the heat for a few minutes, then displays “wait”, then turns off (having never reached the set temp) the furnace for a few minutes, and the heat goes back on again. I know the wait times are settable, but I didn’t understand why the heat was going off before the set point was reached.

Going through the installer menu, I found the “Fan Type” setting to be “Gas”. Just to try, I set it to “Electric”, and all is well. My heater no longer short cycles.

My system is a single-stage central air HVAC, gas furnance forced air.

Question: Is there a such thing as a GAS fan??

Is the correct Fan Type setting for my system in fact Electric?

Thanks.

The gas and electric for the fan is referring to the type of unit it is. if it is a electric furnace or a heat pump the thermostat turns the blower on, if it is a gas furnace the furnace turns the fan on, usually on a lower speed so maybe that is why your furnace is kicking out before it reaches set point, it might be tripping on a high limit, check your air filter or make sure enough floor vents are open.

Gas furnaces also have retained heat. The fan turns off when the heat exchanger cools. Some thermostats have heat anticipatory setting to turn the heat off early expecting the gas furnace to blow more hot air for a while.

Thank you both for the replies. That makes more sense. For me, having a gas furnace, I see that it should be on “gas”.

I’m running into something puzzling:

For heat, the thermostat behaves as expected if the set point is at 72 or below. At 73 or above, the thermostat would start and run the heater for a minute or so, then displays “wait” and shuts off the heat regardless whether the set point is met. After the set “wait” period (5 min), the heat comes on for a minute or so again, and shuts off. The cycle repeats, but the set point is never reached because the heat does not runs long enough.

I’m wondering if there is a firmware issue w/ the Trane unit. It does reboot randomly.

Any ideas?

It sounds like the Thermostat is also set in HeatPump mode.
In this mode it will not allow the unit to come back on for 5 minutes (configurable) to keep the compressor from coming on with a starting high head pressure. (Saves the compressor!).

[quote=“RichardTSchaefer, post:5, topic:178125”]It sounds like the Thermostat is also set in HeatPump mode.
In this mode it will not allow the unit to come back on for 5 minutes (configurable) to keep the compressor from coming on with a starting high head pressure. (Saves the compressor!).[/quote]

The mechanical setting is set to “Gas/Elec”, not heat pump. The minimum time for the “wait” period is 5 minutes. Perhaps it does not differentiate between heater and AC, so it applies the waiting period regardless?

In any event, would you consider the short cycling I described above to be a thermostat fault?

check for any loose connections on the thermostat wire on both the thermostat and in the furnace, the thermostat should never reboot.

Thanks you. My Trane has randomly rebooted from day one with solid wiring. However, your suggestion got me thinking, which lead to more observations, and discovery. The 24V source consistently drops out for about 30 seconds every time the heater starts. I’ll start a different thread…