I’m trying to control 3 tube motors using a single Fibaro FGR221 roller/shutter controller. This saves a lot on wiring headache, not to mention it being nice to be able to control 3 blinds using 1 device on Vera. However things are not working as expected.
I have wired up 3 motors in parallel using 2 multi-pole isolation relays: when the wire for the “up” direction is energised, one relay isolates the individual “down” wires to each motors, and the same happens when the “down” wire is energised. The problem is: when I hit the up or down button, the blinds move a tiny little bit and then the Fibaro shuts off the motor. (The Fibaro is configured for monostable switches, by the way).
Test 1: To verify the wiring, I’ve removed the Fibaro and just wired the up/down switch directly to the motors. This works fine: the blinds move up and down and stop correctly at the end positions. This confirms that the wiring and relays are correct.
Test 2: I have also wired up the Fibaro and bypassed the isolation relays. In this case, clicking Up or Down will move the blinds correctly until they reach the end position, at which point they jitter for a while (as expected). When they all settle down at the end stop, the Fibaro shuts off power to the motors. This confirms the Fibaro is working correctly.
Looks like somehow the relay action throws off the Fibaro, causing it to stop the motors. Has anyone successfully used the Fibaro unit in combination with isolation relays?
The FGR221 monitors the motor current to detect when the blinds reach their limits. Adding the relay has no doubt confused this logic - the low current makes it believe that the blind has hit it’s limit switch so it turns off. You can disable this function by setting configuration variable 10 to 1. Of course you will now have to shut it off yourself with a timer…
A possible work-around would be to connect one motor directly to the FGR221 and use relays for the other two. If you connect the slowest motor directly, the other two should have enough time to reach their stops.
Setting variable 10 did the trick I’ve added a scene that turns off the switch after 1 minute… these things are either up or down; I’ve no interest in lowering them only halfway.
“at which point they jitter for a while (as expected)”, what do you mean by “jitter” and “as expected”, does not sound right, either wrong iso relay or wrong wiring. Risk: blowing a limit microswitch inside the motor or burning the motor itself
“As expected” doesn’t mean “correct” Wiring the motors in parallel without the isolation relay results in a jitter or humming when one of them reaches the end stop. Thankfully this didn’t damage the motors (and looking at the motor’s diagram it shouldn’t). Just did this for testing purposes, to rule out an issue with the Fibaro switch.
With the relay, there is no jitter but somehow the presence of the relay confuses the Fibaro unit, unless I turn off the limit detection feature in the Fibaro.
@shady: I used two simple 4PDT 220v relays; 1 for up and 1 for down. When the “up” power line is energised, the relay disconnects all “down” wires to each individual motor, meaning they are not only disconnected from the “down” power line, but also from each other. You’ll need to put the relay where all the motor cables come together, luckily I already wired it this way instead of daisy chaining the motors.
Misunderstood the fact you were just testing without relays, my mistake.
Glad you you did not insist though, without the relays it would eventually damage the motors.
Good job wiring, FYI even in case the motors are daisy chained, wiring one DPDT in the junction box at each motor location solve the problem too (as long as whatever switches the motors can take the amperage).
It used to be a common electrician mistake (daisy chaining motors), and that is how we solved it.