I have 3 Danfoss LC Z TRV that I have been struggling with, I think they are actually working OK but they never fully close the valve. The TRV seems to get the set point and I think adjusts but they are never quite tight enough on the valve pin to stop water flowing.
The valves are OK as they work with the traditional TRV fitted just not with the LC. I had assumed the radiator valves were all standard but I think my issue must be the design of my valves. I am going through the installation process with LC when I fit the valve, this does tighten them but not enough to close the valve. Has anyone had this? Is it possible to fit a shim or am I going to have to change all of my radiator physical valves?
I had Danfoss but I found them very slow to react, and they didn’t close completely. I’ve recently changed one for a Stella-Z and so far it’s excellent. Radiator stone cold when room temperature is above setpoint and far quicker to respond to Z-Wave commands.
If I recall correctly the Danfoss Living should react instantly when controlled directly, but can take some time to change when changed via Vera.
Does the LC value wobble when when you try to wiggle it (just a little bit ) they should feel quite tight. If there is some movement there then it’s possible they are not sitting correctly.
Thanks for the suggestions. I tried a few things and found that if I add a shim of 1-2mm to the valve pin they operate correctly. The valves will not screw down any further so I can only assumed that my existing physical valves are outside the dimensions that Danfoss anticipate.
When I bought my Danfoss to replace my old thermostats then I also had to replace the small brass piece with the pin. Maybe that is what you are missing.
Thanks Sigge, I agree that would fix it but I would have to drain down the system to change them all. I have a heat store system and it takes ages to drain and refill.