3 Way Lights Switch - GE Kit

Hey all,

I just bought the 3 way kit from lowes, for the IRIS (but i have a veralite). IN the manual, its the 45609 and 45610.

I am controlling my outside garage light, which has a switch in the garage and in the kitchen (seperate structures about 20 feet away) - both had standard 3 way switches before.

I cant get the light to turn on at all, and the master lights up (the blue LED) and licks as if the the relay is kicking - but no light. My question is - does the line AND load wires have to be at the master switch (45609) or can the line be at one switch and the load be at the other?

Through testing my wires with a Multimeter, i found the Feed from the panel at the kitchen switch, but the outdoor light goes to the garage switch 1st. HELP??

Thanks!

The clicking switch indicates that it is miswired, bad, or both, I would not be surprised if the switch is now bad, since it has been miswired.

Yes, the Line and the Load must terminate at the primary switch. The wiring diagram below puts the primary in the kitchen and the remote in the garage.

So am i screwed, or can i re-wire it some how?

Assuming that you have positively identified the wiring, wire it up like the diagram and see if the switch still works.

Is this how your current wiring is? I think i have multiple lights wired like this in my house and I’m trying to figure out how the heck i put in Zwave 3way without rewiring stuff.

Looking to figure it out, hopefully not with rerunning wiring entirely through finished walls.

[quote=“nemix, post:5, topic:178573”]Is this how your current wiring is? I think i have multiple lights wired like this in my house and I’m trying to figure out how the heck i put in Zwave 3way without rewiring stuff.

Looking to figure it out, hopefully not with rerunning wiring entirely through finished walls.[/quote]

Nemix, if that is how your house is truly wired then you can’t use the GE 45609s. These switches need at least 4 wires (hot, neutral, load, and traveler). The problem is your power feed comes in at the light box, if it came in at one of the switch boxes then you could make it work.

All is not lost, you simply need one of the many other z-wave 3-way switches that don’t rely on a traveler wire but instead use a z-way accessory switch to signal the main switch via RF or Z-wave. The Evolve switch is one possibility.

http://store.homeseer.com/store/HomeSeer-Z-Wave-OnOff-Wall-Switch-Comparison-W7.aspx

-TC

Hey guys, still relatively new at this. I have several lights wired as per nemix’s diagram. I was thinking of using this instead:
Aeon Labs Aeotec SC19103-ZWUS Z-Wave Micro Smart Energy Illuminator http://www.amazon.com/Aeotec-SC19103-ZWUS-Z-Wave-Energy-Illuminator/dp/B008VW8NYE/ref=pd_sim_e_3
This would go in the ceiling box above the light. Then I would use scene controllers to operate via Z-wave and Vera Lite.

[quote=“clsanchez77, post:7, topic:178573”]Hey guys, still relatively new at this. I have several lights wired as per nemix’s diagram. I was thinking of using this instead:
Aeon Labs Aeotec SC19103-ZWUS Z-Wave Micro Smart Energy Illuminator http://www.amazon.com/Aeotec-SC19103-ZWUS-Z-Wave-Energy-Illuminator/dp/B008VW8NYE/ref=pd_sim_e_3
This would go in the ceiling box above the light. Then I would use scene controllers to operate via Z-wave and Vera Lite.[/quote]
With a little bit of adjustment to the wiring in the box, this will work fine, providing both manual switched and Z-Wave control of the light. See the attached diagram.